Why doesn't this module count beyond zero after one count?

Why doesn't this module count beyond zero after one count?

Answers

Top answer

This problem occurs because the following parameters are set:

  • Counting limits: 0-32 bits
  • Load value: 0

There are 3 ways you can fix this:

  • Load value greater than 0
  • Setting parameters to a count of -31 to +31 bit.
  • Reset the operating mode parameters to continuous or periodic counting

You know a better answer?

The question about Siemens FM350-1 has already been answered, but there may be a better solution or alternative available by now. If you know it, answer the question now and increase your reputation as an industry expert in our B2B community.