PROFIBUS
Influence PROFIBUS connector with diagnostic LEDs the bus load?
How does a PROFIBUS connector with diagnostic LEDs influence the bus load?
How does a PROFIBUS connector with diagnostic LEDs influence the bus load?
The input impedance of the diagnostic connector is about 1.5 and this is 100 times higher than the impedance of an RS 485 receiver. It should cause neither theoretical nor practical problems.
You know a better answer?
The question about PI PROFIBUS has already been answered, but there may be a better solution or alternative available by now. If you know it, answer the question now and increase your reputation as an industry expert in our B2B community.
What is PROFIBUS termination?
1.9Kviews
What is a PROFIBUS termination and how can be implemented in order to create a power-safe network?
What is the difference between PROFIBUS and PROFINET?
7.5Kviews
What makes PROFIBUS and PROFINET stand from one another, and how can I decide which one should I use in my application?
Why and where is fiber-optic transmission used?
1.3Kviews
Why and where is fiber-optic transmission used?
Was the content helpful to you?