Influence PROFIBUS connector with diagnostic LEDs the bus load?
How does a PROFIBUS connector with diagnostic LEDs influence the bus load?
How does a PROFIBUS connector with diagnostic LEDs influence the bus load?
The input impedance of the diagnostic connector is about 1.5 and this is 100 times higher than the impedance of an RS 485 receiver. It should cause neither theoretical nor practical problems.